NOTE: The presence of overtemperature faults (DTCs B2729, B2730, B272A and B272B) can be induced by
incorrect operation of the climate controlled seat system after an initial heat setting has been attained. If a heat
setting is repeatedly turned OFF and ON in an attempt to increase the seat temperature or repeatedly toggled
between heat and cool modes, an overtemperature condition can result and the DTCs will be set.
If the temperature at one of the TEDs rises above 110°C (230°F) in the heat mode or 65°C (149°F) in the cool
mode for more than 4 seconds, the DCSM will record an overtemperature DTC, remove voltage from the
TEDs and go into recovery mode (blower only) for 30 seconds to cool down the TEDs . The same will occur
if a temperature difference of 60°C (108°F) or greater is seen between the backrest and cushion TEDs on
either front seat. The DCSM will continue to monitor the TEDs while in recovery mode. If the temperature of
the TEDs does not drop to 105°C (221°F) in the heat mode or 60°C (140°F) in the cool mode after 30
seconds, the system will continue to cool the TEDs in recovery mode for up to 5 minutes. If the TEDs cool
down at anytime after 30 seconds, but before 5 minutes (checked at 4-second intervals), the system will
operate as normal. An overtemperature DTC will still be recorded even if the system recovers and is operating
normally. Recovery mode is more likely to occur during extreme cabin temperatures with significant seat back
sunload. If the system does not recover within 30 seconds in heat mode or within 5 minutes in cool mode, the
DCSM will disable that seat (fault mode) and remain off until the ignition is cycled. Also, if the DCSM
detects temperature differential fault twice during the same ignition cycle, it will shutdown. When a fault
causes a shutdown, the climate controlled seat indicators will turn off for the affected seat and that seat will
not be operational until the next key cycle.